How much current can this wire handle?
How big a wire do I need for this much current?
Here's a table from Littelfuse, aimed at automotive uses. Cars are low-voltage, vibration, and somewhat hot, a little like tube amps.
Note that we *never* have to worry about current when picking wires for plate supplies; worst-case a #20 can carry ten times more than the biggest B+ current we are likely to need.
Heater supplies can be an issue. Not for say a DeLuxe, 1.5 Amps, which is off the chart. However an SVT can be pulling 10 Amps of heater current in its big bottles, plus more for the little bottles. Say 12 Amps.
There's two types of wire insulation listed. Unless you are sure, assume the 90 C stuff. (Even THHN house-wire is not technically "cross-link".) So use the "(2)" columns, the "T" column not the "XL" column.
Note the severe de-rating for ambient temperature. I'm rewiring a tractor with a 50 Amp tap. Inside the cab I can almost use #12 (#12 GPT 47A at 25C), so I would use #10. But near the radiator could be over 100 C hot. #6 is a bit small (#6 GPT 47A at 80C), I really should get high-temp wire. In fact my tap is on the cooler end of an open bay, I have 150C rated #6 for the first foot and some tough #8 to run into the cab. Also my max-current (heater blower) will be in the coldest weather when it is zero C in the cab.
Guitar amp guts can run way over 25C but never 100C (we hope).
So for the SVT's 12A, #20 is OK when cool but #15 is needed at 80C. Assuming ventilation, #16 may be OK, #14 would be safer.
Since #14 is very awkward on Octal sockets, you might run the PT leads to lugs, run #16 to the big tube heaters, and #20 to the little tubes. Or even run two #20 to the big tubes in triplets.