Here's the basic hookup for single power/energy meters (attached).
The full load current goes through a very low-resistance coil. Probably your two big terminals, probably near 0.01 ohms. One of your wires goes through here.
The full load voltage goes through a high resistance coil (about 8K). We already have one side of the line, you need another terminal, it carries very low current, so this will be your small terminal. If you are in 120V land, use the 150V term.
If you are in a fight with the power company, it matters which side of the current coil the voltage coil connects to. (i.e. the meter eats some power, who pays for that?) In your case this is irrelevant; just mentioning so if you see it documented the other way, I'm wrong but it still works the same close-enuff.
I sure would start with a lamp limiter, and a lamp load. Start with 25W limit and 60W load. This won't light well or meter well but is safer than a large limiter and should budge the needle off zero.
When that seems fine, no-limiter plus a 100W lamp should read 100W, though I'm not clear what switch and scale to use/read. If you have a heater (not microwave) in the 600W-1000W zone, it should read nearly its nameplate rating. Any guitar amp smaller than a true SVT is within this meter's rating. A Champ should be 50W-60W steady, a 4-6L6 Twin should be 100W idle and 200W when lease-breaking. However the true current drawn is not exactly what this meter reads, there's some reactive current sloshing, so be generous when picking extension cords or fuses.